4/7/2016 3:50 PM | |
Joined: 3/14/2008 Last visit: 9/4/2025 Posts: 2216 Rating:
|
Well, in this case "Abort" means the signal = "1". If you are right clicking the sequencer on the left bottom of the screen and then select: Sequencer properties, it will take you to the correct screen where you can select the start condition.
No, this is not correct, you must get the start condition of the sequencer. You now have set 47SFC1_SEQ(1).ABORT = Abort to the step initialization. That is not correct, you must set this in the starting condition of your sequencer: "ABORT". Access this by right click on "ABORT" in the left bottom of the screen and then select: Sequencer properties. The sequencer will start when the SFC is in Abort and executes the steps in that sequencer |
Last edited by: Oreca at: 4/7/2016 3:57:13 PMIf I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
2 thankful Users |
4/7/2016 3:54 PM | |
Joined: 3/14/2008 Last visit: 9/4/2025 Posts: 2216 Rating:
|
Well, that is a counter block which I do not know off. But normally in a step you have a "Initialization", "Processing" and "Termination" sequence. When a step is activated, all commands under "Initialization" will be processed. Then the step is in the "Processing" step and executes all commands under "Processing". Finally, when the transition of the current step is fulfilled, the step is in the "Termination" sequence. So, if you want to count something, you can set Count=1 in the initialization and Count=0 in the termination. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |
4/12/2016 1:52 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4760 Rating:
|
New question published by AGrS is split to a separate thread with the subject Where I could define an input byte. Best regards |
4/21/2016 9:24 AM | |
Posts: 112 Rating:
|
Also the counter does not work. What do I do wrong if I keep trigger and count_ok on 1 and give count a 1 at the end of my sequence and later make it 0 again? |
4/21/2016 11:07 AM | |
Joined: 3/14/2008 Last visit: 9/4/2025 Posts: 2216 Rating:
|
Hey AGrS! Please observe the SFC OSL. I think I attached this in one of my previous posts... It's the Operate State Logic for the SFC. In the diagram you can see that a Reset command is only valid when the SFC is in the ABORTED state. The SFC is then set to IDLE. The reset in your picture is connected properly. |