7/11/2010 11:17 AM | |
Posts: 8946 Rating:
|
You can do it! Use v/f operating mode if possible, and anything will be fine!. |
This contribution was helpful to
2 thankful Users |
7/11/2010 11:51 AM | |
Joined: 8/21/2008 Last visit: 7/25/2025 Posts: 141 Rating:
|
Hi mef3000, I prefer you to have a look on the previous FAQ. The precautions you need to take care has been described in the linkhere I also need to suggest one more point to this. If the VFD gets failed, then you wont be able to run any of the motor. Hence, if these motor have a critical application please take care of a by-passing contactor to VFD. rgds, RBM |
7/11/2010 11:51 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, I think these links will be useful How could you control different sizes of motors by single drive? How do I use different parameter sets with the MM440/MM430? Best regards. |
Ayman Elotaify |
|
7/11/2010 12:14 PM | |
Posts: 8946 Rating:
|
You are wrong, Ayman Elotaify. Mef3000 told us, that the motors are the same / have the same size. So there is no bigreason for different parameter-sets. Exept, the cable - length and / or the application is very different. |
7/11/2010 2:28 PM | |
Posts: 81 Rating:
|
i ll stop motor and then change contactors but driver ll be on anyway .or should i turn off driver too before changing contactors? |
7/11/2010 2:55 PM | |
Posts: 81 Rating:
|
so normal stop with ramp down will work fine and make no trouble as i get . |
7/11/2010 3:08 PM | |
Posts: 81 Rating:
|
thanks everyone for helping .it has been very helpful for me. |
This contribution was helpful to
1 thankful Users |
1/22/2015 2:02 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4760 Rating:
|
|
This contribution was helpful to
1 thankful Users |