10/7/2016 11:13 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
How V90 is interfaced to S7-1200? Via profinet, MODBUS etc? Please check below FAQ may help you. |
10/7/2016 11:18 AM | |
Joined: 3/12/2015 Last visit: 9/1/2025 Posts: 555 Rating:
|
profinet, and the x8 conector i have cabled like this... |
10/7/2016 12:52 PM | |
Joined: 3/12/2015 Last visit: 9/1/2025 Posts: 555 Rating:
|
. |
10/7/2016 1:30 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Are you sure you have established profinet communication with PLC? How much is the value in p0922 =? Please refer following FAQ for detailed information. Please go thru the Documentation (1,4 MB) file. Speed Control of SINAMICS V90 with SIMATIC S7-1200 via PROFINET |
10/7/2016 1:44 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
OK. So you mean in manual/JOG mode motor is running only in one direction. Assuming this true & refer the wiring diagram you attached in earlier post, it needs to be corrected. Pin 7 i.e. DI 3 is for CWL rotation & pin no 8 i.e. DI 4 is for CCWL rotation. So please correct the wiring. For more information, please refer attached sheets. AttachmentSINAMICS_V90_PIT control.pdf (447 Downloads) |
This contribution was helpful to
1 thankful Users |
10/7/2016 1:49 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, If you want to control V90 with S7-1200 PLC with HMI, please refer below FAQ which will give you detailed information.. SINAMICS V: Controlled Positioning of a V90 with S7‑1200 via the Pulse/Direction Interface, with HMI (Set 7) |
This contribution was helpful to
1 thankful Users |
Follow us on