Hi my friends. ET 200SP, BaseUnit BU15-P16+A0+2D, BU type A0 Siemens 6ES7193-6BP00-0DA0 I have on Channel 0 "Thermocouple, Type K". How do you set the module in the hardware to show the right temperature?Thank you for your help. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/30/2021 07:01:24New subject after splitting |
|
7/29/2021 1:17 PM | |
Joined: 5/22/2015 Last visit: 7/11/2025 Posts: 118 Rating:
|
Hello, you must change the BaseUnit from "6ES7193-6BP00-0DA0" to "6ES7193-6BP00-0DA1" |
7/29/2021 1:33 PM | |
Joined: 1/4/2019 Last visit: 4/1/2025 Posts: 26 Rating:
|
Delivery time is 10 weeks.But I have a Pt100 as a reference sensor. I do not have time. |
7/30/2021 2:14 PM | |
Joined: 3/11/2019 Last visit: 9/1/2025 Posts: 1653 Rating:
|
Hi Tincek1, if you want to use a PT100 for compensation (because you have only BU type A0), please connect the PT100 to channel 0 of the module. As far is i understand the manual, only channel 0 can work as reference (for module, or for group). Please check the configuration as shown in the manual, maybe this helps. Furthermore: - the PT100 has to measure the temperature at connection point - if the thermocouple was lenghtended, the correct compensation cables has to be used (not copper) SIMATIC ET 200SP analog input module AI 4xRTD/TC 2-/3-/4-wire HF Setting: "No reference channel mode" -> "The temperature value at channel 0 can be..." Setting "Reference channel of the module -> "...TC channel uses channel 0" "...must be configured as "Thermal resistor Pt 100 climatic range Degrees Celsius" maybe this helps regards sancruz |
Feedback appreciated, please rate |
|