Hello aleks; Since you are not discussing a Profibus-DP or a Profinet network between your drive and your PLC, you have no need for a gsd file. This is a configuration file for a DP slave that will tell the CPU hpw much data can be exchanged with a particular slave. Since you plan a Modbus exchange (Modbus TCP or Modbus RTU, serial), what you need is the Modbus register mapping for the ATV 600: https://www.se.com/ww/en/faqs/FA294733/ https://download.schneider-electric.com/files?p_Doc_Ref=EAV64328 In TIA Portal, look up the MB_Master instruction (for Modbus RTU, serial connections) or the MB_Client instruction for Modbus TCP (using Ethernet), depending on your physical connection to the drive. Hope this helps, Daniel Chartier |