What you are looking for is: D_ACT_DP It can be used with 300/400/1500 plc's, for deactivate and reactivate configured DP slaves/ AttachmentSTEP 7 Professional V13.1 - D_ACT_DP- Enable-disable DP slaves (1).pdf (392 Downloads) |
Last edited by: Jen_Moderator at: 10/13/2021 08:29:51Added PDF file from link as an attachment. |
|
This contribution was helpful to
1 thankful Users |
10/13/2021 8:56 AM | |
Joined: 8/21/2018 Last visit: 8/20/2025 Posts: 96 Rating:
|
Hello Hati Thanks for your reply, I will try to use this function. But I am also considering to use Library for Configuration Control (LCC) with "LCC_ReconfigSys" function or LAcycCOM Library with "LAcycCom_ActDeactDrive" function. I found manual with examples for LCC: https://cache.industry.siemens.com/dl/files/270/29430270/att_1017489/v2/29430270_LCC_DOC_V201_en.pdf and for LAcycCOM: https://cache.industry.siemens.com/dl/files/270/29430270/att_967139/v1/29430270_Config-Control-Safety_DOC_V10_en.pdf Will it work ? What is the diference between "LCC_ReconfigSys" from LCC and "ReconfigIOSystem" from Extented instructions ? I assume that LCC function uses standard function, but as library have some UDTs and extra logic inside function to facilitate use. Am I right ? Best regards AttachmentPDFs.zip (446 Downloads) |
Last edited by: Jen_Moderator at: 10/13/2021 11:58:51Added PDFs as an attachment. |
|