Which Means Single source can not possible to make 2 CU with 2 SLM. So My configuration is not possible to run??? |
2/3/2022 3:49 PM | |
Joined: 10/11/2006 Last visit: 9/8/2025 Posts: 6039 Rating:
|
Hello, 2 CU with 2 SLM require two galvanic isolated supplies to prevent from circular currents, so your setup would not work.
|