Hello denis.zaifu, maybe, there is someting wrong with serverpackage and/or dcf-files. https://support.industry.siemens.com/cs/ww/en/view/109763043 Then generate the serverpackage new on the Server, and load
Georg Berghof |
PS: If this post did really help you, you may use the Rate-button |
|
2/11/2021 12:00 PM | |
Joined: 7/3/2019 Last visit: 10/19/2022 Posts: 16 Rating:
|
Hello Georg Berghof, i proced the steps and no improvement happend regards |
2/12/2021 12:53 PM | |
Joined: 10/10/2014 Last visit: 8/28/2025 Posts: 1725 Rating:
|
Hi denis.zaifu, Messages: SSM..: unresolved external function The split screen manager function errors are the reason why the picture tree not works on you client pc. This has naffing to do with the client installation Check on your client if you can see the share scriptfct Start -> Execute insert\\computernamefrom you client The scriptfct is the share to the directory C:\Program Files (x86)\Siemens\WinCC\aplib The ssm...fct funktions are located in the directory C:\Program Files (x86)\Siemens\WinCC\aplib\Split Screen Manager Do you insert you window user in the group SIMATIC_HMI ? Best regards schufri |
This contribution was helpful to
1 thankful Users |
2/15/2021 12:51 PM | |
Joined: 7/3/2019 Last visit: 10/19/2022 Posts: 16 Rating:
|
Hi schufri Indeed this was the problem, i solved it and now all works fine. Thank you very much for helping me! |