Hello. I think my answer will not valuable for you, but for another who faced with this task will be. I spent 4 hours for find solution. Most valuable siemens documentation is Process control system PCS 7 High Availability Process Control Systems (page 160). My troubel was that i make wrong connection H system CPs with Plant Bus A and B. Need to connect CP1 with PlantBusA and CP2 with PlantBusB on CPU A, but on CPU B need connect CP1 with PlantBusB and CP2 with PlantBusA. (check box is grayscalled because it screenshoted at cross-project network view).
|