Dear a.aras, The decimal number 16834 on the fieldbus is equvalent to 100%. This is defined in the Profidrive standard. The scaling of the current is calculated with p2002. On plc side 16384 must be scaled with the same value from p2002. A detailed description is available in the operating instructions of the DCM under chapter 10.3. Please find this document under the following link: https://support.industry.siemens.com/cs/document/109825291/sinamics-dcm-dc-converters?dti=0&lc=en-WW |
With best regards, |
|