Hi, please refer to theoperating instructions, and theParameter List[Function Diagram 3100], all the information you require is available here. To set the MOP up to accept DIN2 as MOP+ and DIN3 as MOP-, set the following: P700=2 (Terminal Control) P702=99 (BICO Control, DIN2) P703=99 (BICO Control, DIN3) P1000=1 (MOP Setpoint only) P1035=722.1 MOP Up P1036=722.2 MOP Down Hope this helps, Graeme
|
10/16/2010 6:29 AM | |
Posts: 19 Rating:
|
Dear Graeme Thank you very much. Regards haque_1981 |