Hello, please check, that P590 is "0" and P556,557,559,and 560 do have high level in Index 1. When you are operating in speed control mode, please ensure, that the possition control is disabled by P210=0 and / or P772=0 You can open a case at the customer support (https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo2&siteid=cseus&lang=en&aktprim=99&nodeid1=16605022&siteid=cseus&extranet=standard&viewreg=WW&groupid=4000003) describe your problen and send them your parameters list. |