Hi, the cable for serial connection is 9ak1012-1aa00. You can also backup the drive via Profibus if you have this capability - i.e. Profibus adaptor and Drives ES. P60 needs to be in Mode 7 which means free upread and "Carefull" - Download Regards, Graeme
|
1/26/2013 10:53 PM | |
Posts: 4 Rating:
|
Hi Graeme thanks for you response,i was helpful Anyway If you don't mind I have a question for you regarding your response... I've already took parameters from the project Plc exporting the parameters as well... I've been thought that throught the projetc Plc with the drive Ed package I could had make downloading at the Masterdrive MC plus,but I don't know how to do it....I figured out also that via the profibus adapter is a solution with higher cost.. If you could help me,that's would be appreciated Ciao Kind regards Peppe |
1/27/2013 6:57 AM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Hello Peppe, In case you have DriveES package installed. If your drive is connected via Profibus to PLC and you have an Entrnet connection to CPU from PC there is possibility to 'reach' the drive directly. Take a look athttp://support.automation.siemens.com/WW/view/en/14929205 Best regards, Hristo Mihalev
|