Hello, if you want to go online with the drive you have to have a connection cable. If you don`t have one, you can make a own cable - see capture 5.5. http://support.automation.siemens.com/WW/view/de/13472409/0/en First I would make a upload and save the parametrization. Note p350, p352, p352, p353 and p354. In P97 is the motorcodenumber. Now you should have p97 = 41. The other motor has the condenumber 37, so set p97=37 (before set p60 = 5). So I would choose the following sequence: p60 = 5 p97=41 p60=7 p350 .... p 354 (set to the original values). So if you don`t have the drivemonitor, you could change the parameter by the PMU. Note: You have a other motor and the characteristic of your machine could be changed now - so maybe you have to do some optimizations (for example other Inertia, ...). But this depends on your application too, if that has an effect. |