Hello Bantik; You should be able to connect a Vegaflex 61 as a 2-wire sensor, but first, which power unit do you have installed in the sensors? See the screenshot below. The information for the Vegaflex sensors is taken from the following document: https://www.insatech.com/downloads/FLEX61-62-66_Solid_29658-EN.PDF Note that the ET 200S module is simply a 2-wire analog input, without HART. So you will read only the primary HART variable from the connected sensor. Hope this helps, Daniel Chartier |