6/1/2011 4:39 PM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
Hello Oscar_83PL,Yes it is. Hot swapping (replacing module online) is available in S7-400 CPU whether you work with central modules (S7-400) or S7-300 modules (Profibus & Profinet). With S7-300 CPU, it's available but just with Profinet. Or maybe you can use the trick mentioned here
Best regards. H-H |
Last edited by: H-H at: 6/1/2011 4:41 PM |
|
This contribution was helpful to
1 thankful Users |
6/1/2011 7:03 PM | |
Joined: 8/5/2009 Last visit: 7/4/2022 Posts: 156 Rating:
|
I don't know much about hotswap possibillities But I just worked with a new type S7 CPU 6ES7 315-2EH14 V3.2.3 This CPU has Profinet IO If you look at the online Technical data it is possible to use OB83 (only for Profinet IO ) Technical data new 315 PN DP |
6/2/2011 9:08 AM | |
Joined: 10/7/2005 Last visit: 9/4/2025 Posts: 3049 Rating:
|
you can swap, add and/or reconfigure in RUN with CIR (Configuration in Run)dear Oscar_83PL and you'll find all the relevant info (what hardware is supported/needed, whatis possible and what isn't) in the manuals and links below: SIMATIC STEP7 V5.5 Modifying the System during Operation via CiR manual Which DP slaves can be added to and removed from a PROFIBUS DP master system using the CiR function (Configuration in RUN) and which configuration changes are permissible? What should you watch out for when adding components or changing their parameters using CiR (Configuration in Run)? What should you watch out for when using the "Configuration in Run" (CiR) function on the PROFINET IO system? |
Cheers |
|
This contribution was helpful to
2 thankful Users |
6/3/2011 8:15 PM | |
Posts: 947 Rating:
|
Hello! I believe thatCiR is only available for CPU4xx or am I wrong? |
6/4/2011 2:26 AM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
Hello gre_m, No, you are not. The CIR is only availablewith S7-400 CPUs. Best regards. H-H |
6/4/2011 6:20 PM | |
Posts: 947 Rating:
|
Hello I understand your reply. I wanted to say "The CIR is only availablewith S7-400 CPUs". May be defect translate. |
Last edited by: gre_m at: 6/4/2011 6:22 PM |
|
Follow us on