3/10/2020 2:53 PM | |
Posts: 9 Rating:
|
I would like my RTU to be able to read the value of the LOGO! network output function block which i have set to VB:1, bit: 1 |
3/10/2020 3:03 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
Who ist the server, who is the client? |
3/10/2020 3:09 PM | |
Posts: 9 Rating:
|
i am communicating Modbus/TCP to a remote device which is an RTU (data concentrator) |
3/10/2020 3:22 PM | |
Posts: 9 Rating:
|
I came across this in another post. i will try this addressing schedule; see attached pdf which i believe implies V1.1 will be at coil 10: AttachmentModbus Table.pdf (581 Downloads) |
This contribution was helpful to
1 thankful Users |
3/10/2020 5:13 PM | |
Joined: 2/22/2008 Last visit: 4/25/2025 Posts: 2698 Rating:
|
Maybe the original file will help you, see attachment. There is also an excel sheet and you can type in any bit, byte or word on the right side (see column M/N). But first select the start address in J1 (0 or 1) to get the right values for the complete table. The start address depends on the Modbus partner. Regards, Scorp AttachmentModbus Tabelle.zip (383 Downloads) |
This contribution was helpful to
1 thankful Users |