8/23/2016 5:42 PM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
Hi, Have a look at the Configuration Control (option handling) in the central or distributed configuration I hope I could help! |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to
1 thankful Users |
8/24/2016 10:30 AM | |
Posts: 8 Rating:
|
Thanks it is what I was looking for :) |
8/26/2016 2:34 PM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
Hi, I do not want to disturb the discussion. Anyways I have comment to make: If you can not use the examples due to V5.4 compatibilty issues, why not use the "oldschool" way like Activate/deactivate the DP slave's based on the requirement. See System Software for S7-300/400 System and Standard Functions Volume 1 and Volume 2 manual under chapter "16.3 Deactivating and Activating DP Slaves/PROFINET IO Devices with SFC 12 "D_ACT_DP"". |
- What you read here, please check with manuals and your requirements. |
|