3/4/2020 10:54 AM | |
Joined: 7/31/2009 Last visit: 7/19/2025 Posts: 13 Rating:
All, Can anyone please suggest where to start troubleshooting the errors in the attached? HW diagram and address assignments to follow... Attachment04032020Diagnose.txt (388 Downloads) |
3/4/2020 10:56 AM | |
HW diagram... |
3/4/2020 11:24 AM | |
Address assignments...AttachmentPU109 Station Addresses.txt (384 Downloads) |
3/4/2020 11:31 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
Hello, you have an FM module with address 736, where is? have a OB 82 loaded to the CPU? |
3/4/2020 12:35 PM | |
Yes, At address 736 there's a FM 354 SERVO module in Rack 3/Slot 10. |
3/4/2020 2:31 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
hi, you need to go online and have a look to the module with adress 736. There´s a channel error detected. You can also capture the diagnostic alarm with OB82 and SFC51. Have a look to this FAQ: With diagnostics-compatible modules how do you evaluate a change of the diagnostics status in the user program of the S7-300?hope this helps, regards, |
FCK WAR! |
3/4/2020 3:56 PM | |
mopS04, Attached is OB82. |