9/16/2008 6:21 PM | |
Posts: 487 Rating:
|
When you did your HW config, did you use "Edit->insert redundant copy" to create DP master system on the second PLC? |
11/7/2008 1:37 AM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
Dear Gaurav Kharadi, In step 3, station B was Master and IM was assigned to station B, that's why IM-2 is the active one. In step 4, there's a Redundant Link Failure, (I'm not sure of this explanation but this is what I have in my mind) According to SWR manual, when there's Redundant link failure, the DP slaves stay with their previous master. SO, in step 4 the IM stayed withits previous master which is station B. That's why IM-2was active and IM-1was not active. This is completely wrong and when you have such situation you must interfere by yourself and activate IM-1 and then I recommend to restart CPU A. After restart, you will have Station A asMaster and the IM will be assigned to the right new master (IM-1 will be the active one). I believe step 5was based on a wrong situation (step 4)and that's why it doesn't work well. Try to correct the situation when you come to step 4 and try doing step 5 after that and tell us the result. Best regards.
|
11/14/2008 7:37 AM | |
Posts: 52 Rating:
|
john Enthu I think your CPUs' version are V2.6.x,is it? UPdate them to 2.1.x or 2.0.x Regards, Hannibar |