4/8/2022 6:43 PM | |
Joined: 9/14/2021 Last visit: 1/31/2023 Posts: 99 Rating:
|
So PT100 sensor is as same as RTD & TC sensor? |
Just with a floral skirt♥♣, and nothing else |
|
4/9/2022 1:41 PM | |
Joined: 9/27/2006 Last visit: 9/11/2025 Posts: 12405 Rating:
|
Hello Hassan Sabbah; You have 2 ways to connect a RTD/TC temperature sensor to a Siemens S7 AI module: - you connect it directly to a RTD/TC AI module (with or without compensating wire). These specialized AI modules are designed to read the very low mV signals from these sensors, in which case you divide the input signal by 10.0 to read the temperature value in centigrade, as you can see in the tables of Ch. 5 of the S7-300 module data manual. - you add a RTD to 4-20 mA converter (or a TC to 4-20mA converter) between the sensor and the 4-20 mA AI module you are using in the S7 rack.in thst case, you have to scale the 4-20 mA signal to a temoerature result, and then ypi need FC105 "SCALE". See the RTD to 4-20 mA converter from this manufacturer, as an example: https://www.pepperl-fuchs.com/canada/en/classid_1827.htm?view=productdetails&prodid=894 Everything will depend on the configuration of the PLC and you choice of AI module. I have already proposed the S7-300 module data manual, look at the specifications of the analig input modules (and the signals they are designed to work with) in ch. 6. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 04/09/2022 15:56:04 |
|
This contribution was helpful to
1 thankful Users |
4/10/2022 7:02 AM | |
Joined: 9/14/2021 Last visit: 1/31/2023 Posts: 99 Rating:
|
Thanks again!! Now I fully understand. |
Just with a floral skirt♥♣, and nothing else |
|
Follow us on