4/5/2019 1:19 PM | |
Posts: 17 Rating:
|
Here it is. As I said before, IPs are ok, I can even download screens to panel. thanks, |
4/5/2019 1:27 PM | |
Posts: 17 Rating:
|
Also, I have like 80 devices connected to my network and I have needed to set up manually the update time in some of them, maybe it is a similar issue? thanks, |
4/5/2019 2:40 PM |
|
Posts: 2826 Rating:
|
. |
Last edited by: #dP at: 4/5/2019 2:41:15 PMLast edited by: #dP at: 4/5/2019 2:41:58 PMTS attaches project making message redundant. |
|
4/5/2019 2:40 PM | |
Posts: 17 Rating:
|
TIA version is 15 hmi image version is also 15. |
Last edited by: JosephSan at: 4/8/2019 3:23:53 PM |
|
4/8/2019 1:05 PM | |
Posts: 17 Rating:
|
Here it is, friends, sorry for the delay. I am still unable to get connection with PLC. :(
Attachment19-20458_HMI_Test.zip (340 Downloads) |
4/8/2019 1:08 PM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, same as before , no ap15! How you crewate the archive? Regards Christoph |
4/8/2019 3:20 PM | |
Posts: 17 Rating:
|
Ok, Now it is as you said... I did not know I could archive Siemens files like this, and I had to remove almost everything. Thanks, Attachment19-20458_HMI_Test_6.zip (330 Downloads) |
4/11/2019 10:12 AM | |
Posts: 17 Rating:
|
Solved! IT was that I did not select the "connection" label on the device network, so that is why it was not making the connection atomatically. Thanks. |