11/15/2016 1:06 PM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
Hi, See the SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modules manual under chapter "6.2 Diagnosis of Faults of F-SMs [ID: 431591819]" If you need further help, save the diagnostic of the module in question and upload it to us. |
Last edited by: MicroMan at: 11/15/2016 1:15:07 PM- What you read here, please check with manuals and your requirements. |
|
11/16/2016 10:46 AM | |
Joined: 11/4/2015 Last visit: 9/10/2025 Posts: 16 Rating:
|
There are no errors on the DO module. That is why the SF LED is blinking. To remove the blinking and turn SF LED off the system requires an acknowledgement. This acknowledgment is initiated through safety matrix however the SF LED will not stop blinking.
|
11/16/2016 11:14 AM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
See theSIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modulesmanual under chapter "6.2 Diagnosis of Faults of F-SMs [ID: 431591819]" You can read: a flashing of the SF-LED in safety mode means a request for depassivation. It makes me believe you have spare channels on that card. As they are not configured in the matrix, matrix can not reintegrate the channels. I hope I could help! |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to
1 thankful Users |
11/17/2016 10:10 AM | |
Joined: 11/4/2015 Last visit: 9/10/2025 Posts: 16 Rating:
|
I understood from the manual, "The SF LED flashes until you acknowledge passivation following a module fault." Since Safety Matrix acknowledge driver feature clears the passivation indication in the software but on the hardware the SF LED flashes there must be a way to find out from the program what is the reason. Diagnostics are empty. "It makes me believe you have spare channels on that card" I have other modules with spare channels and there is not problem with them when it comes to Safety Matrix acknowledging and getting rid of SF LED flashing.
|
11/18/2016 9:37 AM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
Hi, This must be caused by something specific in your application. If you save us the XREF->Addresses list we will see if there is channel driver being configured for spare channels or not. Maybe that is causing the issue. I suggest you contact Siemens Support to make sure you get support you need. |
- What you read here, please check with manuals and your requirements. |
|