9/15/2008 8:35 AM | |
Posts: 2348 Rating:
|
Diagnostic address is input address. So you bump into max.input address restiction - it's CPU dependant. You can't avoid it. |
9/15/2008 10:13 AM | |
Posts: 2348 Rating:
|
You can say so but in fact it's diagnostic address limit. |
9/16/2008 4:04 PM | |
Posts: 162 Rating:
|
Hi, the CPU has only one PN-IO. What would you change? Aret has anything to say. Best regards FrankW |
9/16/2008 5:40 PM | |
Posts: 487 Rating:
|
I have not used RF660R, but after looking thru the program this iswhat I understand. It uses open TCP communication to PLC. The program uses internally TCON to establish the connection. So the parameters you enter in DB300 are usedas the connecton parameters. So you need toenter IP address of the RF660 at DB300. DBW 148 to 151 Since you have 192.168.3.251 it will be rem_start_adr = B#16#FB, B#16#03 B#16#A8 B#16#C0And for remoteport # 10001 (this should be same as the port # you configured in RF660)
The local port # is set at local_tsap_id= B#16#22 B#16#4E This value 4E22 (hex)= 20002 |
9/17/2008 12:21 PM | |
Posts: 19 Rating:
|
Thank you very much JMJ. Now, I have no problem with my system. The major problem was a time stamp conflict issue. I corrected the problems. The system goes perfect :) |