can't get tsend or put/get to work... how can it be so hard to share variable over diffrent plc in the same network? |
1/28/2025 5:38 AM | |
Joined: 10/7/2005 Last visit: 9/2/2025 Posts: 3049 Rating:
|
The screendump is hard to read but it seems you configured an S7 connection and then use (try to) use AG_SEND/AG_RECV. This will not work and you need to either change you connection to ISO-on-TCP (or TCP or UDP or ISO) as per example that you followed OR use BSEND/BRCV if you want to stick with an S7 connection. For reference and anything you ever (or never) wanted to know about communication within the Siemens PLC world, grab a copy of the CPU-CPU communication with Simatic Controllers |