5/10/2021 11:08 PM | |
Joined: 8/11/2018 Last visit: 11/8/2024 Posts: 2 Rating:
|
Hi, I tried to get the actual torque value from S120. I get the value from TO a LREAL value but i didnot see the change of the value i put a NOM_X with (0-16834) an Scale_X(0.0-38.36) because that is my Reference P2003, that es correct? when i put -16834 to 16834 i have a straight value from sinamic. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/11/2021 10:07:44New subject after splitting |
|
5/11/2021 8:40 AM | |
Joined: 10/11/2006 Last visit: 8/29/2025 Posts: 6037 Rating:
|
Hello, when using Telegram 750, you get the actual torque as systemvariable at the TO automatically. 4.1.2.2 Configuration - Data exchange with the drive (S7-1500, S7-1500T) Supplementary data Select the "Torque data" check box if you want to configure the data connection of the torque data. If you have selected a drive with which the additional telegram 750 has been configured, the "Torque data" check box is preselected. A.1.13 "StatusTorqueData" tag (speed axis) (S7-1500, S7-1500T) https://support.industry.siemens.com/cs/de/en/view/109766462 |
With best regards, |
|
This contribution was helpful to
1 thankful Users |
1/22/2025 1:57 PM | |
Joined: 3/2/2007 Last visit: 8/28/2025 Posts: 990 Rating:
|
Kindly, is this actual Torque, as read by the S7-1500 plc, in percent or in Nm or ? |
... thank you ... |
|
3/17/2025 3:08 PM | |
Joined: 12/14/2011 Last visit: 7/24/2025 Posts: 176 Rating:
|
Hi, look at the picture... |
Follow us on