Hello magnus; What communication module are you using as a Profibus master in your project? A S7-1200 CPU does not support Profibus natively, it requires a CM 1243-5 to act as a Profibus master. Here is a link to the CM 1243-5 manual, and below is a video showing how it needs to be configured (the module setup section starts around the 4:25 mark). https://support.industry.siemens.com/cs/ca/en/view/49851842 I suggest you take the time to show us (with a diagram) how you are setting up your Profibus network presently, we may see what is wrong in your project. Take the time to alsop tell us why you want to use Profibus instructions designed for the S7-300 (SFC 14 and 15, using Step 7 v5,x), we may be able to help you figure out how similar operations are programmed in TIA portal. Hope this helps, |