Hello I am new for s7-1200 and pid. I write a pid. Set point consatan. Input are change but cant see output. Evert time is 0.0 Pls give me advice Best Regard Nec |
| 6/30/2010 8:49 PM | |
|
Joined: 3/21/2006 Last visit: 1/10/2026 Posts: 10247 Rating:
|
Hello, Look and check according to SIMATIC STEP 7 Basic V10.5 SP2 (from page 649th) . best regards, Hristo Mihalev |
| 7/1/2010 1:08 PM | |
|
Joined: 9/23/2005 Last visit: 1/15/2026 Posts: 4447 Rating:
|
Hi, check if the PID is not in manual operation and ifit is inactive ( “sReti_mode”). There is a TIP about PID: /tf/WW/en/Posts/33957#top |
|