Dear Expert, How can I activate FFB activate by AOP in Sinamics G130. Regards Pranab |
6/4/2011 11:39 PM | |
Joined: 9/18/2006 Last visit: 5/31/2025 Posts: 596 Rating:
|
Hi. Can be so: 1) CU p9=2 2) CU p108 [0].18 = 1 (bit 18) - Activate FFB CU 3) CU p108 [1].18 = 1 (bit 18) - Activate FFB object 1 4) 3) CU p108 [2.18 = 1 (bit 18) - Activate FFB object 2 etc Check: CU p108 [1].18 = 1; Object 1 r108.18 = 1 Then you change 20000-20999, that is necessary to you. Best regards. AttachmentG130 FFB.pdf (448 Downloads) |
6/5/2011 8:41 PM | |
Joined: 9/18/2006 Last visit: 5/31/2025 Posts: 596 Rating:
|
Hi. You install the Starter. You use the DCC in G130. DCC has more functionality than the FFB. Best regsrds. |
6/6/2011 9:09 AM | |
Joined: 9/18/2006 Last visit: 5/31/2025 Posts: 596 Rating:
|
Hi. Hi. You select the "CFC 7.x" when installing the "Starter". You get the authorization to "CFC". That's all. Working. This is my example of a project Sinamics S120. AttachmentExample DCC in project Starter.pdf (432 Downloads) |
6/6/2011 10:07 AM | |
Joined: 9/18/2006 Last visit: 5/31/2025 Posts: 596 Rating:
|
Hi. You need to declare variables. Best regards. AttachmentDeclaring variables.pdf (435 Downloads) |
6/7/2011 8:22 AM | |
Joined: 9/18/2006 Last visit: 5/31/2025 Posts: 596 Rating:
|
Hi. I found the description (creating customer-specific parameters "declare") in the documentation. Best regards. AttachmentCreating customer-specific parameters-declare.pdf (459 Downloads) |