(1)| 9/17/2011 7:54 PM | |
|
Joined: 12/27/2006 Last visit: 11/17/2025 Posts: 1200 Rating:
|
You have invert the R(eset) input of the RS Block (B001) Its only works if I2 is always ON. The R(reset) on the RS laching Block has more prio than the S(set) Thus when Set AND Reset both are 1 the output is 0 Nex time, you make a .zip of your programm, and post it here, so we kan test it. Look at the attachment AttachmentRS-Display.zip (473 Downloads) |
| 9/17/2011 10:41 PM | |
|
Posts: 2 Rating:
|
Hi, Yes, it is correct that I have inverted the I2 input since my stop button is NC. Problem is that when I simulate the program in LSC everything work as it should. It's not before I have downloaded the program to the LOGO itself, the problem appear. regards, Jon AttachmentCircuit Diagram2.zip (451 Downloads) |
| 9/18/2011 7:24 PM | |
|
Posts: 134 Rating:
|
you have to change the properties off the input I2 ,from switch ( make contakt ) to push button AttachmentRS DISPLAY.zip (481 Downloads) |
| 9/19/2011 10:02 PM | |
|
Posts: 134 Rating:
|
why is a bug i logosoft v7? even in v6 you are not able to display the status ( on-off ) of the fb! |