(0)| 12/11/2012 11:33 AM | |
|
Posts: 8092 Rating:
|
What is rating of MCP? In another workshop, does the MCP trips in both the cases?, means when starting in Y & when starting in D. |
| 12/13/2012 12:27 PM | |
|
Joined: 10/22/2008 Last visit: 12/23/2025 Posts: 378 Rating:
|
MCP is 22Amps setting. The fuuniest thing is that mcp does not trip if i start it directly in star nor delta. It only trips during transition from star to delta. The cabling is checked and all is doe with recomended wiring of phases by siemens. http://www.automatyka.siemens.pl/docs/docs_ia/Zestawy_rozruchowe_gwiazda_trojkat_dla_silnikow_pradu_zmiennego_1.pdf |
| 12/13/2012 12:43 PM | |
|
Posts: 8092 Rating:
|
Please increase the time in star. In star the motor should run for 15 seconds & then to switch over to delta. Set accordingly & then check. |