Hello, for a consistent project, you need an existentPQWfor the configuration of the TO. You can use a free I/O area in you project, e.g telegram extension of the CU or drive. See chapter 7.1.6 Setting an axis as a real hydraulic axis without a valve (axis simulation) http://support.automation.siemens.com/WW/view/en/99007017 |