8/24/2015 5:40 PM | |
Posts: 3 Rating:
|
Thanks for your help, I assume I can use the mathematical calculation block by calibrating the PT100 and putting an offset value in? |
8/24/2015 7:21 PM | |
Joined: 12/27/2006 Last visit: 8/26/2025 Posts: 1200 Rating:
|
Yes. Look in the attachment. If your PT100 always xx degrees to high (long wire?) then you can corrrect it. In the attachment, the temp is correcting by -4. Becouse there is 1 digit (digital placement =1) it wil be - 0,4 degrees. Adjust in the mathematical instructin (B002) AttachmentCircuit Diagram6.zip (461 Downloads) |