11/28/2016 4:29 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35962 Rating:
|
Here is a possible solution.
AttachmentFill_level.zip (580 Downloads) |
This contribution was helpful to
1 thankful Users |
11/28/2016 5:08 PM | |
Posts: 200 Rating:
|
Hi Thanks for the quick reply. this is what i had but not the scaling block. what is this used for. AttachmentAI TEST.pdf (545 Downloads) |
11/29/2016 9:57 AM | |
Posts: 200 Rating:
|
hi i have attached the manual for the float page 4 is the one we are using. VEGASON S 61 Attachmentvega-line-PriceList_GB.zip (506 Downloads) |
11/29/2016 1:25 PM | |
Posts: 200 Rating:
|
liquid |
11/29/2016 2:02 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35962 Rating:
|
What is the maximum fill level of the tank? This limit can be parameterized at the sensor. And after the set value, the parameterization is carried out in the logo program. Attachment32944-EN-VEGASON-S-61.pdf (572 Downloads) |
11/29/2016 3:40 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35962 Rating:
|
Here is a solution. The distance is scaled to 3.75m because the sensor must have a minimum distance to the medium of 0.25m. The analog input number depends on whether you use an analog input module and how many analog inputs are enabled on the basic module. AttachmentFill_level_V2.zip (368 Downloads) |
This contribution was helpful to
1 thankful Users |
12/8/2016 3:07 PM | |
Posts: 200 Rating:
|
Hi i have the 2 AIs on the base ticked and then used AI3 the sensor i have been sent has a 2 wire output |