6/29/2016 8:44 AM | |
Posts: 64 Rating:
|
Hi expert . In Simoreg 6RA70 in operation mode ( Run ) sometimes we have fault F043 . we use Simoreg for breaking operation . what is result of this fault ? |
6/29/2016 9:41 AM | |
Posts: 64 Rating:
|
thank you . Is it related to the return voltage from the coil of motor when voltage is removed from motor ? |
6/29/2016 11:45 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
It is back EMF of DC motor. Please read this link for more information. Please check the current in r019. During torque reversal when current is too high drive trips on F043. The reason is motor back emf is too high that is why drive injects more current so as to stop motor. But when this current exceeds 100% it trips. HTH. |
6/30/2016 11:45 AM | |
Posts: 64 Rating:
|
Sometimes this fault bothers me and it repeats frequently . how can I repair this fault ? |
8/3/2016 10:26 PM | |
Posts: 64 Rating:
|
I think this formula is better for calculating Resistance of conductors . R=r L/A R is the resistance of the conductor in Ohms A is the cross sectional area in m2 L is the length of the wire in meters r is the resistivity of the material in Ohm(meters) Also U can check this link |