4/22/2009 3:53 PM | |
Joined: 4/1/2009 Last visit: 9/4/2025 Posts: 29 Rating:
|
HI In the zip file is how I set a NAV and som about a electric motor which I am using. I using incremental encoder from LARM firm , it is IRC 200/1000 . Its parameters: 1000 pulse/ 1 rev it have to signal A and B with phase quadrature I using the LiYCY 5*0,25 FACAB 50104 cable and usin SU 13 to interconnection EXM 438 with IRC. Best Regards POLIP Attachment1.zip (672 Downloads) |
4/23/2009 11:19 AM | |
Joined: 8/31/2005 Last visit: 8/8/2025 Posts: 2198 Rating:
|
First pleaseset the You wrote you have aIRC 200/1000 from LARM. I found this. You must check you have the IRC202/1000 or the IRC205/1000 Depending you have the IRC202/1000 or IRC205/1000 encoder type you have to addjust the DIP switches in the EXM348: see here in chapter 2.2.5 The IRC202/1000 needs +-15V and the IRC205/1000 needs +-5V setting. |
Last edited by: miami at: 4/23/2009 1:25 PMcorrected the connector name |
|
4/23/2009 1:32 PM | |
Joined: 4/1/2009 Last visit: 9/4/2025 Posts: 29 Rating:
|
How can I restart the FM? |
4/23/2009 1:50 PM | |
Joined: 8/31/2005 Last visit: 8/8/2025 Posts: 2198 Rating:
|
The easiest way is to switch the S7-400 rack off and on. |
|
|
Follow us on