9/4/2012 5:13 PM | |
Joined: 7/7/2010 Last visit: 9/9/2025 Posts: 16077 Rating:
|
This comment, "8 fast inputs and 4 HSC counter..." is why 2 or 3. 8 fast inputs means PLC rather than add-on module inputs. Check this thread for details on the S7-1215: /tf/WW/en/Posts/73271 To read A&B channels for speed/direction, that's 2 HSCs per encoder, and 8 fast inputs is one PLC with a few inputs left over. To me, that's 3 PLCs, but you might find a way to get by with just 2. There may be some industrial piece of hardware that just detects encoder direction and provides a 1/0 output based on relationship between A-A'/B-B' -- and canbe put to a regular plc input and save on HSC inputs. |
science guy |
|
9/4/2014 10:41 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4760 Rating:
|
New question published by Arun Thakur 3499is split to a separate thread with the subject How to configure HSC to count in both directions?. Best Regards Min_Moderator |