8/30/2013 9:49 AM | |
Joined: 5/12/2006 Last visit: 9/15/2025 Posts: 22710 Rating:
|
Hello, do you mean the PN LED on the SIMOTION or on the S150? How are the LED's on the SIMOTION? Do you use RT or IRT? Please post a the SIMOTION Diagnostic Log when the S150 is powered on. Normaly there should be an event like "Station comming". Regards Christoph |
8/30/2013 11:03 AM | |
Posts: 17 Rating:
|
thanks for the reply! The flashing PN LED is on s150 while the pn led on simotion is off. The pn led on simotiom is also off even when they are in normal communication without problem. it's using RT.
|
8/30/2013 11:12 AM | |
Joined: 5/12/2006 Last visit: 9/15/2025 Posts: 22710 Rating:
|
Hello, an the SF LED on SIMOTION? Can you post a Diagnostic log? Regards Christoph |
8/30/2013 2:12 PM | |
Posts: 17 Rating:
|
I don't have much information. It's a project in foreign country. I support it remotely. I will ask for the diagnostic . |
9/1/2013 4:09 PM | |
Posts: 17 Rating:
|
Dear ChristophD, I got some new information from on site. There are five S150 connected to SIMOTON D445. Not all S150 have this problem. The first and the fourth CU320 are the exception. They can get back to Profinet communication automatically with D445 while the other three are the ones with problem. For example, when the second CU320 repowered, the PN LED on CU is flashing in green and the PN LED on Simotion is Flashing in red. The sf LED on Simotion is always off no matter how the profinet communicaiton is. attached is the diagnostic information. the send CU is described as CU320(2). I really appreciate if you could give some suggestion. Thanks very much! BR
Attachmentpn.zip (723 Downloads) |
9/1/2013 6:07 PM | |
Joined: 5/12/2006 Last visit: 9/15/2025 Posts: 22710 Rating:
|
Hello, please use the SIMOTION Scout to save the Diagnostic Log of the PLC. In the Simatic Manager are not enough informations to analysze the problem. Regards Christoph |
9/4/2013 4:01 AM | |
Posts: 17 Rating:
|
Hi, ChristophD, I got the diagnostics buffer from Scout. It's the same as the diagnostics of Simatic. It seems there are not so many information we have. BR ihui
|
9/4/2013 4:30 AM | |
Joined: 5/12/2006 Last visit: 9/15/2025 Posts: 22710 Rating:
|
Hello, please use the "Save As" Button to save the diagnistic log. a screenshot is never really helpfull in this case. Regards Christoph |
9/4/2013 5:05 AM | |
Posts: 17 Rating:
|
Hi ChristophD, It normally takes some time to get feedback from on site. Before that, I would like to know if we have to config the topology in the hardware configuration? The option box ' assign IP address via IO controller ' is chosen in S150. All the PN devices including one simotion and five S150 are all connected to a scalence X208. In their program X208 is not configured. Could you please tell me in which cased the topology should be configured? I uploaded the program in the attachment. Many Thanks! BR ihui
|
Last edited by: ihui at: 9/4/2013 7:54 AM |
|
9/4/2013 7:52 AM | |
Joined: 5/12/2006 Last visit: 9/15/2025 Posts: 22710 Rating:
|
Hello, the topology must be configured in the following cases: IRT is used the Option "Support device replacement without exchangeable medium" is set with a configured topology the controller know the place of each device an if a device is replaced by a new on. What you can check: when the S150 is powered up scan the PROFINET network , have all devices the correct name? In you screens i see thats the error occurrs on press1 and press4. How is the topology between the simotion an the s150 devices? Regards Christoph |
9/4/2013 3:04 PM | |
Posts: 17 Rating:
|
Hi ChristophD, I am glad to tell you that the problem has been solved after they config the topology. The option of replacement with new device was selected in their project. As you said the topology configuration is necessary in this case! Thanks so much for your help! You are always the one who gives answers. BR IHUI
|
Follow us on