10/14/2010 5:15 AM | |
Joined: 8/25/2006 Last visit: 8/22/2025 Posts: 2218 Rating:
|
Hello. Look at the manual of Simoreg. First I recommend you to reset all parameters to default values (chapter 7.4 of manual), then go to the chapter 7.5, where is described how to setminimum required parameters. If you connect your drive to Profibus, then look at chapter 7.7.2. |
10/14/2010 5:16 PM | |
Posts: 8 Rating:
|
Thanks for KSN. Iwill try.if you have a few examples of this problem.you could send me references? Thank you very much and good luck!
|
10/15/2010 3:32 PM | |
Posts: 8 Rating:
|
DearMuthamizh.S! Thank you very much! I hope to get many of your comments. Good luck~! Best Regards. |
11/29/2010 12:48 PM | |
Posts: 8 Rating:
|
Dear KSN and Muthamizh Selvan ! My system uses 2 Simoreg for 4 motor control. That is 600A and 1200A. for Crane System. But Today. When I am working with Simoreg.the following errors: 1) In Simoreg 1200A: The parameter : R70=108 6RA7085-6FV62-0 R72=600A while i use Simoreg 1200A : 6RA7091-6FV62-0 So While working DC-Simoreg 1200A is appear F031 error. I can't setting R70 =110 ! Please help me! Thanks you so much! |
11/29/2010 12:57 PM | |
Posts: 8 Rating:
|
Dear KSN and Muthamizh Selvan ! Here. This is Parameter :I set: AttachmentChanges only.pdf (939 Downloads) |