12/21/2018 4:01 PM | |
Posts: 15 Rating:
|
HI parada, do I need to connect the adapter before installation of SIMATIC ? Thank you. ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 12/29/2018 11:37:29 AMNew subject after splitting |
|
12/27/2018 11:26 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, which PLC you have? Christoph |
12/27/2018 11:34 AM | |
Posts: 15 Rating:
|
Hi, Im using SIMOREG DC-Master 6RA7018 and Technology module T400. |
12/27/2018 12:21 PM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, in the manual of the adapter https://support.industry.siemens.com/cs/ww/en/view/16983464 you need 24V from the MPI Interface. Pin 2 M24V Pin7 P24V you can use a external power supply like 6es797-0ca00-0xa0 The CBP2 have no 24v support! Regards Christoph |
12/27/2018 12:44 PM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, yes with the PC Adapter USB A2 you can solve this problem. https://support.industry.siemens.com/cs/ww/en/pv/6GK1571-0BA00-0AA0/pi?dl=en Regards |
This contribution was helpful to
1 thankful Users |