(0)| 3/17/2021 8:31 PM | |
|
Posts: 4 Rating:
|
Hi, I am experiencing a communication issue of WinCC V7.2 project with PCL CPU416-2 DP (6ES7416-2XN05-0AB0) + CP443-1 (6GK7443-1EX20-0XE0). I have no acces to the real PLC, so I run the PLC project in S7-PLCSIM Prof. 2010 SR4 (V5.4 SP5 Upd.2). An error message in the WinCC\Diagnose\SIMATIC_S7_PROTOCOL_SUITE_01.LOG file is "Cannot connect to "LineMaster": Errorcode 0xFFDF 42C2". Siemens SW installed is as follows: TCP/IP connection parameter in WinCC is as The PLC Ethernet interface setting is as The PLC is online Is any idea, please? ------------------------------------------------------------------------------------------ |
Last edited by: Lvovich13 at: 03/17/2021 20:38:55Last edited by: Jen_Moderator at: 03/18/2021 09:28:46New subject after splitting |
|
| 3/18/2021 9:56 AM | |
|
Posts: 7298 Rating:
|
Hello Lvovich13, the Errorcode 0xFFDF 42C2 means If you use S7-PLCSIM, you should set the logical devicename the "PLCSIM" see FAQ "How do you simulate S7 Communication between two S7-1500 CPUs using S7-PLCSIM?" https://support.industry.siemens.com/cs/ww/en/view/88781327 Regards Georg Berghof |
| 3/19/2021 6:44 PM | |
|
Posts: 4 Rating:
|
Hi Georg, I found the Logigal device name setting and changed it to PLCSIM. It works now. Thnaks a lot. |