(0)| 5/31/2021 12:12 PM | |
|
Joined: 10/11/2006 Last visit: 1/16/2026 Posts: 6068 Rating:
|
Hello, yes it is possible. When using no PLC it is necessary to use DCC for the logic, and TB30 or TM31 for a analog input. DCC https://support.industry.siemens.com/cs/ww/en/view/109776202 For controllling the setpoint for torque limiting value, you need "Technology Controller" to compare actual torque with the torque setpoint. 9.1 Technology controller https://support.industry.siemens.com/cs/ww/en/view/109781535 Yes, the simulator is basically a motor in regenerative mode. To deactivate monitoring you have to set P1545 = True; This depents on the resolution of the external torque sensor. Yes, it will rotate, because motor has no power. Torque limit = 0; |
|
With best regards, |
|
This contribution was helpful to
|
|