(0)| 8/1/2022 9:26 AM | |
|
Posts: 101 Rating:
|
Dear expert, In PCS7 V9.1, I am facing below issue for Alarm banners- Does anyone already come across such issue? Please find attached image- Regards, Zankkar |
| 8/3/2022 9:10 AM | |
|
Joined: 5/3/2017 Last visit: 12/5/2025 Posts: 673 Rating:
|
Hi Zankkar, can you tell us what is your problem with the alarm banner? I can't see any problem. The strike through message are a normal behavior of WinCC if the message from the AS is already due while starting the process execution of the operator station. Date and time do not correspond with the date and time at which the message in the automation system resulted, so the invalid date and time will show as strike through (see the manual PCS 7 OS Process Control at the section Structure and States of Messages). With regards |
| 9/18/2022 7:39 AM | |
|
Posts: 101 Rating:
|
HI Heisenberg2, Thank you for response and sorry for a late reply. Actually if you observe column, Column width is not full. This happen after migration to V9.1 SP1. Regards, Zankkar
|