Hello. As fare as I can tell from the 802D manual and 611 manual Direct measuring systems HAS to be connected to X412 on the Servo card. You can not setup the use of X461 and X462 and transfer it to the PCU This limits your ability to choose a TTL encoder, since X412 needs to be either 1Vss SIN/COS or Endat encoder. Please see attached picture. Manual is on this link:802D: Turning, Milling - Commissioning Manual |