Hi alex-macabu, at first i would recommend to extend the program (error + status) as described in following FAQ. Otherwhise a "potential" error with its status can not be seen the way it is used at the moment. How do you evaluate the status of system blocks in STEP 7 (TIA Portal)?
Please check afterwards, if there is another status written into the seperate static tag. regards sancruz |
Feedback appreciated, please rate |
|
12/16/2022 5:03 PM | |
Joined: 10/11/2019 Last visit: 7/28/2024 Posts: 27 Rating:
|
That was a very valuable tip! After using a MOVE instruction to store the error code in a DB I was able to see that the TSEND_C was outputing the 80C6 which means that Remote partner cannot be reached. Now I can at least troubleshoot what might be happening. Probably this laptop has a firewall that is blocking the PLC. I will check and answer this thread as soon as I find the issue! Thanks for the tip!
|