(0)| 4/25/2023 5:05 AM | |
|
Joined: 1/21/2013 Last visit: 1/20/2026 Posts: 4416 Rating:
|
Hi aktsarabdikar, Since I do not know Movicon Next, it is not easy to answer your question. However, since you mentioned OPC UA, I assume that you need OPC UA functionality for your S7-1200 PLC. Starting with TIA Portal V16 and firmware version V4.4, the S7-1200 CPUs come with OPC UA server functionality. To use this functionality an additional runtime license is required for each CPU. Kind regards |
This contribution was helpful to
|
|
| 5/4/2023 10:25 AM | |
|
Joined: 8/3/2009 Last visit: 1/19/2026 Posts: 16644 Rating:
|
Hello aktsarabdikar as an additional information you can have a look at this Link: https://support.industry.siemens.com/cs/de/en/view/109781701 Bye Murof |
|