(1)| 5/30/2023 4:20 PM | |
Hello hsocarras; I suggest you open this link, and download the example for get/put between a S7-1200 and a S7-300, it also applies to your CP 343-1 Lean: https://support.industry.siemens.com/cs/ca/en/view/82212115 Start by examining the addresses attributed to both Ethernet partners in the project, pages 6-7. Notice the IP addresses are distinct and unique; start by correcting that part of your program. Possibly that solves your issues. If not sufficient, compare the rest if your setup with the example program. Hope this helps, Daniel Chartier |
| 5/31/2023 6:36 AM | |
Joined: 3/11/2019 Last visit: 1/7/2026 Posts: 1653 Rating:
Hi, did you change the TSAP rack/slot in configuration of S7-connection? How you configure a connection in the TIA Portal?"Set the partner Connection resource to 03 and Rack/slot to the partner CPU. Even if a CP is slotted with the partner, the CPU is always addressed with the Rack/slot." regards sancruz |
| 5/31/2023 8:33 AM | |
Joined: 9/26/2020 Last visit: 11/18/2025 Posts: 12 Rating:
Brilliant, that solved the problem. |