Hello, The mentioned statmnt is correct. I think we are talking here on PM340 with MLFB: 1SE11-3UA0, attached picture that showing its technical specification. So, as we can see, rated input current with line reactor is 1.3 A. rated input current without line reactor is 1.7 A. Thus because normally the line reactors limit lower frequency harmonics that are fed back into the supply. Also they used to smooth the voltage spikes. so the current will be lower in case of using these line reactors. Here's attached a data sheet for line reactor and you will found in it which line reactors should be ordered with which power modules. In your case, it should be: 3CC00-2AD3 Regards, AttachmentLine Reactor.zip (372 Downloads) |