Hello again, I tried the same program with KTP400 + TIA Portal v15.1 and it seems to work too. I noticed that it simulates the program differently than with TP1200 panel. I attached the demonstration, in which the value change works as I want it to with internal tags. Attachmentbuttbit.zip (513 Downloads) |
10/14/2019 7:49 AM | |
Joined: 7/31/2019 Last visit: 6/5/2025 Posts: 6 Rating:
|
Thank you very much, that makes sense. |
3/19/2025 8:31 AM | |
Joined: 7/5/2013 Last visit: 9/10/2025 Posts: 3241 Rating:
|
Hi, for changing the screen of the basic panel you may use the job mailbox, no. 51. E.g. SIMATIC WinCC WinCC Advanced V14 SP1 - Communication The way you described it, you would have to consider
Regards, Frink |
Pi is exactly three! |
|
3/21/2025 9:23 AM | |
Joined: 8/3/2009 Last visit: 9/10/2025 Posts: 16386 Rating:
|
Hello If you work with a Tag trigger in the HMI that should work in the background then you have to set the acquisition mode to cyclic continous (use the largest cycle that is OK for you to prevent communicaiton load) Also check this FAQ for basic help: https://support.industry.siemens.com/cs/ww/en/view/93909293 Bye Murof |
If this Information really helps, you could use the Rate function |
|