Hi, here the link to the S7-200 system manual. Hope this helsp: http://support.automation.siemens.com/WW/view/en/1109582 |
| 6/17/2010 10:01 AM | |
|
Joined: 10/7/2005 Last visit: 1/22/2026 Posts: 3054 Rating:
|
Hello Rizal Dwi Listio Do notbother trying to find a hardware modul as a replacement for the 6ES5380-8MA11 Timer Module. This Timer module simply creates two (not even very accurate) PLC internal pulse timers without any external wiring. I suggest you replace the module by pure Timer logic implementation in the S7 PLC. You'll find the functional description of the 6ES5380-8MA11 Timer Module in the S5-90U/S5-95U Programmable Controller System Manual (see Function module chapter 16). I hope this helps |
|
Cheers |
|
| 6/17/2010 10:40 AM | |
|
Posts: 77 Rating:
|
hi fritz, can you suggest me how i can setting the timer value? |
| 6/18/2010 8:42 AM | |
|
Joined: 10/7/2005 Last visit: 1/22/2026 Posts: 3054 Rating:
|
Hello again Rizal Dwi Listio I must honestly say that I do notquite understand your question. It should be as simple as putting in Pulse Timer into your S7 logic,give it the sameTime Setpoint as what was on the "wheels" of the Timer card and use internal bits instead of the Timer card I/O's to start and check it I hope this is the answer you were seeking but if not please try to explain your problem in more detail. |
|